FESApprentice2496
Member
I was at a Job and the nameplate rating on the outdoor unit was 25 A Fuse or Circuit breaker. well they dont make the convenient equipment discconect in 25A...its always 30 or 60... what we have to put there is a 60A non fuse disconnect... SO my question is... is it okay to put a DP 25A breaker at the main panel run 10/2 to the equipment disconnect and go into the 60 A non fuse disconnects we have?