a/c disconnect

Status
Not open for further replies.

tbiertze

New User
Which of the following is not acceptable for an a/c disconnect? 50' from the condensing unit, inside the house, I know the answer is inside the house because it has to be within sight and readily accessible, but I can not find if 50' away is acceptable. Any help??
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
You need to look at Article 100:

In Sight From (Within Sight From, Within Sight). Where this Code specifies that one equipment shall be ?in sight from,? ?within sight from,? or ?within sight,? and so forth, of another equipment, the specified equipment is to be visible and not more than 15 m (50 ft) distant from the other.
 