laramie said:and unfortunately this particular customer doesn't care about cost- they want the problem fixed.
laramie said:Hey all, thanks for taking the time to help. Here's the scenario; we have a large residential project we completed some time ago. The homeowner is complaining that when the (4) A/Cs kick on, the lights in the entire house go dim. There is a 400A 120/240V service on the house, and a total of 3 subpanels. THe ACs are run from a remote subpanel on a 2nd floor. This has gone as far as a) the utility company has come and set a new transformer outside, b) the breaker feeding the sub panel has been relocated from the lighting breakers, c) ampereage and voltage have been measured and found to be within limits..
We're out of options. Would a voltage regulator/stabilizer, and/or a power conditioner help? If so, where would i find one that can effectively monitor an entire house? I imagine this would be a common problem in factories, hospitals, etc... how do they deal???
Any help would be appreciated!
winnie said:The RTISS system uses filtering techniques to precisely synchronize to the line and properly time the triggering of the semiconductor switch, even in the presence of power quality problems. By doing this, when the dimmer is set for 50% output, it will remain at 50% output.
As far as I can tell, there is nothing in the document which describes an attempt to _compensate_ for supply voltage fluctuations.