I'm becoming confused as to when a non-fused versus a fused disconnect is required for a typical 480V/3PH rooftop AHU.
Typically, I size these units with a non-fused disconnect located at the unit and size the wire and circuit breaker according to the namplate MCA and MOCP respectivly.
However, another Engineer in my office insists that we design with a fused disconnect using the MOCP as the fuse size (located at the unit). The wire and circuit breaker are sized according to the namplate MCA and MOCP respectivly.
To me, it seems like you are oversizing your required protection by providing MOCP fuses at the disconnect AND circuit breaker.
I thought that proper MOCP sizing of the circuit breaker was enough to not have a fused disconnect.
I've looked all over NEC 2002, but nothing really jumps out at me.
Thanks in advance for any help!