12/2 NM and a 30 amp OCPD. MC cable 14/2 and a 30 amp OCPD with 75° C terminations.
I"m drawing blanks on how 14ga wire can be used here. Any help would be appreciated....
If going by earlier code cycles you can even do 14/2 at 60*C :angel:
Does the wire need to be rated at 125% of the minimum circuit ampacity?
As mentioned 12 is minimum, 14 once would have been minimum, but with 90 feet you may want to consider voltage drop and maybe end up running 10 anyhow.MCA nameplate rating on a 3 ton unit -18.7 A
Max Breaker Ampacity 30 A
Wire size = 10/2 or 12/2 NMB ??
90' length