cadpoint said:Whats an MCA, Oh and was that before of after some percentages ?![]()
#12 is good for 30 amps in this case 240.4(g) unless you are using nm cable.normbac said:If the mca on a A/C condensor is 25.4 amps can you round down to 25amps and use a #12 cu
or must you round up to 26 amps and be required to use a #10cu
Or not round anything and still be required to use #10cu
Oh and was that before of after some percentages
Dennis Alwon said:#12 is good for 30 amps in this case 240.4(g) unless you are using nm cable.
The nameplate has 125% in it already
infinity said:#12 is only good for 25 amps even if you're using NM cable. You can't use the 30 amp rating since it's at 90 degrees C.
Dennis Alwon said:I stand corrected, of course you are right. Lord knows what I was thinking- going from memory- bad idea in my case.![]()