Or am I mistaken, and we can construct a reasonable example where a normal sized EGC depends on a minimum impedance of the ungrounded conductors in order to be adequate during a fault?
If I had the time I would.
Thinking about this some more, it seems to me that if are concerned about conductors/EGC surviving a bolted fault, what we end up with is a criterion of a minimum conductor size based on the available fault current.
That is, if for sufficiently large fault currents, the OCPD opens (say magnetically) in a fixed time period (say 1 cycle), then the worst case I
2t would occur when I is the full available fault current. E.g. for a fault immediately after the OCPD where the impedance contribution of the conductor and EGC between the OCPD and the fault is small enough to be negligible.
Then the temperature rise of any conductor carrying the fault current (including the EGC, which is likely the smallest conductor in the fault current path) will depend on I
2t/A
2, where A is the cross sectional area. The square factor arises as one factor due to decreasing resistance with area (and thus decreasing power dissipation per unit length I
2R and thus decreasing total energy I
2Rt), and another factor due to increasing conductor mass per unit length, and thus increasing energy required to raise the conductor temperature a given amount.
The result is that if there is a maximum allowable conductor temperature rise (say, that the EGC does not get hot enough to damage the insulation of other conductors it may be in contact with), we get a maximum allowable I
2t/A
2, which coupled with a worst case maximum fault current I and a fixed t in the instantaneous range gives us a minimum allowable A.
So then why doesn't the NEC have a rule of the form "given an AFC of X, the minimum conductor size is Y"? I mean, I haven't worked out an example of the above (partially because I'm unclear why the formula in post 100 has logs in it and is missing a square exponent on A; seems like for short time spans the heat generated has no time to be conducted away and the right hand side should just be proportional to the temperature rise), but surely it will say that with a 50,000A fault a #14 conductor would experience excessive temperature rise?
Regardless, getting back to the point of 250.122(B), it seems to me that the result is that if for a given circuit with a given size EGC, the EGC will avoid excessive temperature rise during a fault located anywhere on the circuit for any fault current in the instantaneous OCPD range up to the AFC, that same statement will be true even when the ungrounded conductor is upsized. As in either case, the worst case is that the fault is just after the OCPD and the fault current is the full AFC, and so it's the same worst case.
Cheers, Wayne