Re: A few panels minus two
Originally posted by m73214:
George.....So running boards are horizontal 2X4's spaced kind of like ladder rungs between the top of the panel and the top plate of the wall? Sorry, I've never come across the term before.
Don't be sorry or bashful at all. There are sometimes items or techniques we use every day that we never learn the "code term" for. I have posted this message in the thread, as there might be other folks out there who don't know and would greatly benefit from the discussion.
Imagine a receptacle outlet in a normal bedroom, where you drill a hole in the top plate, and run the romex straight down the wall into the box. When you staple the romex to the stud the box is nailed to,
that is what a running board looks like.
The NM is snug against the 2x4 (or whatever you use) for the duration of the space where it needs protection.
Think about a basement, where it would be real easy to just get in line with the other trades, and run a trunk line down the center of the basement with the HVAC, plumbing, gas pipe, etc. You can't run small cables that way (334.15(C)), because they'd get damaged. Why? Coat hangers, skis, lumber, there are all kinds of stuff the occupant would hang or leans on the cables.
If you nail up 2x4's connected end-to-end along side the plumbing, HVAC, etc, then you can use them as running boards to follow the same path.
How you use a running board is open to interpretation. Some AHJ's interpret that you must staple cables to the side of a running board in a basement. Others will fail an installation unless you staple to the bottom of the board. It
is open to interpretation.
Would they be required on both sides of the wall?
No, a single board protects NM from all directions, in theory.
I assume if the area is being drywalled, there is no need for them?
Correct. Then, you fall back on support every 4.5' and within 12" of every box (or 8" of a single gang with no clamps).
[ January 14, 2006, 09:56 AM: Message edited by: georgestolz ]