Confession time:
I am an idiot. This may not come as a surprise to many, but it feels good to confess it.
On my project, they poured all the foundations for the sixplexes, trenched in all the service laterals, and whatnot, in 2003. At that time, they intended to build in a clockwise rotation through the neighborhood. They (whoever they are) decided to build three in that manner, and then, in their infinute wisdom, spun around and began building in the opposite direction.
As a result, a set of garages sitting in the middle of the parking lot, serving two different sixplexes, had conduit running to the wrong building. The building that was originally intended to supply the garage is not going to be constructed for a long, long time.
Looking at the predicament, I decided the easiest route was to divert the conduit to a nearby transformer, and install a service lateral (instead of an outside feeder).
I got the okay from the POCO, sold the GC on the idea, and called for a trencher. I discovered upon digging down for the conduit that the jac***s that originally installed the sleeve under the street installed a 1" conduit for the garages. I was intending to install a 100 amp service to the garage. I had already picked up the Square-D 100 amp all-in-one metermain with 8-spaces below.
At that point, my mental design changed from a conduit run to direct burial, since the spot marked on the curb was a good two feet from the actual sleeve, and my trench hooked a hard 100?+ turn to find it, on both sides of the street. :roll:
Upon finding the 1" conduit, I checked the fill tables, and found the most I could put in there was a 4-3 URD (USE's). So, now I was going to install 60-amp conductors, which was okay by me, since it was above my estimated load. I thought that since my conductors were sized for the connected load, and service conductors were unprotected at their source anyway, then I could install a 100 amp metermain and forget about it.
I was unaware of the existence of 230.90, and the fact that the service conductors are considered protected by the load side of the conductors. I broke with my habit of trying to fail the unusual installation I was considering before I proceeded.
Then it passed inspection.
Stupid! Stupid! Stupid! 
I am an idiot. This may not come as a surprise to many, but it feels good to confess it.
On my project, they poured all the foundations for the sixplexes, trenched in all the service laterals, and whatnot, in 2003. At that time, they intended to build in a clockwise rotation through the neighborhood. They (whoever they are) decided to build three in that manner, and then, in their infinute wisdom, spun around and began building in the opposite direction.
As a result, a set of garages sitting in the middle of the parking lot, serving two different sixplexes, had conduit running to the wrong building. The building that was originally intended to supply the garage is not going to be constructed for a long, long time.
Looking at the predicament, I decided the easiest route was to divert the conduit to a nearby transformer, and install a service lateral (instead of an outside feeder).
I got the okay from the POCO, sold the GC on the idea, and called for a trencher. I discovered upon digging down for the conduit that the jac***s that originally installed the sleeve under the street installed a 1" conduit for the garages. I was intending to install a 100 amp service to the garage. I had already picked up the Square-D 100 amp all-in-one metermain with 8-spaces below.
At that point, my mental design changed from a conduit run to direct burial, since the spot marked on the curb was a good two feet from the actual sleeve, and my trench hooked a hard 100?+ turn to find it, on both sides of the street. :roll:
Upon finding the 1" conduit, I checked the fill tables, and found the most I could put in there was a 4-3 URD (USE's). So, now I was going to install 60-amp conductors, which was okay by me, since it was above my estimated load. I thought that since my conductors were sized for the connected load, and service conductors were unprotected at their source anyway, then I could install a 100 amp metermain and forget about it.
I was unaware of the existence of 230.90, and the fact that the service conductors are considered protected by the load side of the conductors. I broke with my habit of trying to fail the unusual installation I was considering before I proceeded.
Then it passed inspection.