That is interesting that you say that because I feel it was a loose connection from the factory. The breaker was never used until this piece of equipment was hooked up and even at 13A on a 15A breaker, the buss should not have burned up the way it did. I literally saw the connection glowing and arcing as the current was being pulled through it and the breaker didn't heat up enough to trip. This was a bolt in type breaker factory installed. As far as a 15 or 20 on the circuit, I know that they would protect the load at 13 or 18 amps, but sometimes not all the time, they plug in another Auatherm and at 13 amps a piece and a 30A breaker needs to be in place because how long will a 26A load last on a 15 or 20 amp breaker. This is the only reason why we use the 30A breakers, it allows us to be versatile when connecting this equipment because we can't pick and choose what mold goes where but when it is put into service we have to be ready to make sure it performs properly wherever it winds up.