We have a 4" EMT conduit that turns the corner of a building via an LB. The conduit carries (3) 500 MCM copper conductors to a 250 kW solar inverter.
We know that one of these wires is bad: the upstream OCPD has tripped 4 times since it's been in operation, and a megger test shows a lower reading on one feeder. I suspect that the fault is in the conduit between the LB and the inverter (pictured in the bottom left of the photo). The reason I believe that the fault is in that section is because the installation contractor installed the LB the wrong way for the direction of their wire pull (red arrows). So instead of pulling out the side inlet of the LB and then into the back outlet of the LB, they pulled out the back and then into the side.
I observed them during the pull and they had a hell of time getting those 500 MCM wires through the LB. The difficulty of the geometry was compounded by the fact that they didn't bother to use any wire-pulling lube, which was typical for their pulling practices on this job. (The wire was not SimPull or any other pre-lubricated product.) As they got to the final few feet of wire going through the LB, the wire loop really jammed up hard on the inside corner of the conduit body. They were using a Bobcat front loader to pull the wire through the final 90 deg sweep into the side of the inverter, and they snapped their pull rope. (No tuggers or tension calcs on this job!) After the rope broke, the crew finally heeded my advice and slathered some wire lube on the problem area. Finally, they were able to get the wires pulled in, but I'm sure the insulation got damaged during that fiasco.
So now we plan to disassemble the conduit from the inverter pad to the LB and inspect the wires. If we find the damaged area and the rest of the wire tests good, then we'd like to install a splice box in place of the LB (or just before the LB). But I don't know if there's a narrow, rectangular, weather-proof splice box that will fit inline with that 4" conduit. Unfortunately, they ran EMT conduit for the solar DC feeders both above and below the 4" AC feeder conduit, so that prevents us using a standard square box.
Any recommendations? Here is another view of the conduit run: