I have encountered an issue i would like sopme input on.
480v to 208/120 45kva dry type step down transformer, feeding a 150a contactor, which in turn feeds a 150a load center with a main.
It's using 1/0 cu
a phase between the contactor and load center main is getting so hot you can not touch it... Slowly burning the insulation off.
Current measures at 45-50 amps on all three legs. Nuetral current is 40a +-.... Panel is ballanced fairly evenly. Loads are mostly electronic gaming equipment.
The conductor on a phase is very hot to the touch. No apparent problems on b&c.
All terminations were pulled loosed and checked. Nothing obviously wrong here either.
Transformer does not appear to have any hot spots. Primary current seems normal. All voltages are normal. Bonding jumpers in good condition, and bonded to xo, a ground rod, and building steel, as well as having a properly sized equipment grounding conductor, which is bonded as well.
What do you think could be causing the heating?
It's using 1/0 cu