Can someone help me with this?
Situation:
A 42kA rated wye-delta starter of a chiller is fed from a 1600A feeder breaker of a 100kAIC rated substation via 60ft long 4 sets 500kcmil cables. The available fault current at the starter is 63kA > 42kA.
Questions:
1) Can cable limiter be used at both ends (feeder breaker and starter) of each cable per phase to reduce the short circuit? Bussman do make cable limiters for industrial applications.
2) For the above described single line diagram, do I need to worry about series ratings NEC 240.86?
Thank you very much.
Situation:
A 42kA rated wye-delta starter of a chiller is fed from a 1600A feeder breaker of a 100kAIC rated substation via 60ft long 4 sets 500kcmil cables. The available fault current at the starter is 63kA > 42kA.
Questions:
1) Can cable limiter be used at both ends (feeder breaker and starter) of each cable per phase to reduce the short circuit? Bussman do make cable limiters for industrial applications.
2) For the above described single line diagram, do I need to worry about series ratings NEC 240.86?
Thank you very much.