a "roundhouse"ran to three gfci outlets=tripping

Status
Not open for further replies.

zappy

Senior Member
Location
CA.
so me and my dad ran this and the gfci's tripped when you had a load on them.why?would you guy's agree that it's not a good idea to use a mwbc feeding gfci's?
 

iwire

Moderator
Staff member
Location
Massachusetts
zappy said:
so me and my dad ran this and the gfci's tripped when you had a load on them.why?

They are wired wrong or they are working and the load has a fault.


would you guy's agree that it's not a good idea to use a mwbc feeding gfci's?

No, I will not agree, I do it quite often

A MWBC can supply GFCI receptacles.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
zappy said:
so me and my dad ran this and the gfci's tripped when you had a load on them.why?would you guy's agree that it's not a good idea to use a mwbc feeding gfci's?

If you are feeding receptacles with a MWBC and the GFCI Breaker are 2 single poles then this will not work. You would need a DP GFCI breaker.
 

stickboy1375

Senior Member
Location
Litchfield, CT
zappy said:
so me and my dad ran this and the gfci's tripped when you had a load on them.why?would you guy's agree that it's not a good idea to use a mwbc feeding gfci's?


So why dont you explain how you wired them and maybe we can help you with your problem...
 

zappy

Senior Member
Location
CA.
12-4 to the first gfci outlet,12-3 to the next,12-2 last

12-4 to the first gfci outlet,12-3 to the next,12-2 last

is there a better way?thanks
 

mdshunk

Senior Member
Location
Right here.
zappy said:
12-4 to the first gfci outlet,12-3 to the next,12-2 last
Did you pigtail to each receptacle? If you pigtailed, your arrangement will work fine. If you have anything on the load side of those GFCI's, you caused your own problem.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
stickboy1375 said:
Why the 12-4?


Three circuits. This will work fine with GFCI receptacles if wired correctly. It's no different than the 3 phase, 4 wire feed to the panel.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
stickboy1375 said:
The last time I saw a "roundhouse" was with Patrick Swayze in the movie Road House... :grin:
Funny back at ya! That was on TV this morning. :)

And, no, I'd never give a sarcastic remark. Not me.
 