Hello All,
I have an RTU unit that is rated for 480V main lennox. We are adding an ionization device on it that requires 24VAC and the load is only .41A or 10 watts. The lennox is providing a small transformer rated 480V primary to 24VAC secondary rated for 75 VA somewhere inside the unit and it has a protection 3.5AMP circuit breaker (on secondary). The transformer catalog number 42w94, model LB-74930.
My question is: wouldn't i also need a primary fused on this transformer? and if so what should it be? and what type?
Thank you,
I have an RTU unit that is rated for 480V main lennox. We are adding an ionization device on it that requires 24VAC and the load is only .41A or 10 watts. The lennox is providing a small transformer rated 480V primary to 24VAC secondary rated for 75 VA somewhere inside the unit and it has a protection 3.5AMP circuit breaker (on secondary). The transformer catalog number 42w94, model LB-74930.