That depends on whether the same conductor size is used. The additional current without PFC may require a larger sized conductor.Because the extra current leads to additional I^2R losses all the way from the service to the load.
Actually, that's one of the justifications for fitting PFC at the installation stage.
On one project we are currently undertaking there was a significant saving by fitting PFC close to the load allowing us to drop the cable size.
Obviously this isn't the situation if the PFC is a retrofit.