yes it is a wye-wye dry type S0 from square d. labels: high side, 220/380, low side, 120/208, 40KVA. low side powers a panel with electronic non-continuous single phase loads and UPS's in a gov't facility. the hook up diagram inside is missing. it's taps are labeled H0-H1-H2-H3 and X0-X1-X2-X3.
whomever hooked it up brought 3 phases and a ground from the panel feeding the high side. they hooked the ground to H0 and H0 is jumpered to X0. XO is tied to the enclosure as per NEC, bonding of separately derived systems.
PROBLEM(?)-there are 9 amps on the green wire feeding H0. the other end of this green is on the ground bar of the distribution panel.
extensive research on square d's tech library fails to find any info on this particular model. i think it is custom made. but square d references a different wye-wye tx they make and call for H0 and X0 to be tied together with a removable strap.
even if i were to bring a neutral to this tx, assuming i have to tie H0 to X0, and i bond X0 to the EGC per code, i will still have amperage on the ground, correct? the neutral i run and the ground will simply share the imbalance from the secondary, no?
there is no way to balance the secondary given the single phase loads it carries.
it would seem to me that there is no way to get the ground unloaded. anyone know anything good? surely the code prohibits this nonsense? anyone? bueller?