An existing installation uses Allen Bradley Flex EX I/O to interface to field IO in a Class I Div 2 area (Flex Ex is in the Div 2 area, as are all of the field devices). The Flex-Ex is overkill for a Div 2 area, however it is what is installed.
The plant needs to interface with a non-i.s. solenoid, and proposes to install an interposing relay between a 1797-OB4D output and the device. The proposed relay is listed for Div 2 installation but is not marked IS.
I have stated that the relay is not listed for use on the I.S. installation, and is not a simple apparatus.
- Would a relay coil be considered 'simple apparatus?
- If I/S relay coil is required to connect to the 1797-OB4D module, does such a relay exist? I looked quickly at MTL and did not see anything.