Eddy Current
Senior Member
Anybody know the code reference that mentions what to do with abandoned circuits? I remember seeing it in there before, but can't find it now.
Other than maybe Cellular Metal Floor Raceways and Cellular Concrete Floor Raceways I cant think of any.
Seems like I remember something about abandoned circuits after removing receptacles.
The only other places in the code, besides what Iwire mentioned, that mentions abandoned cables or conductors is in Articles 640,645,725,760,770,820, and 830.
I had this discussion with an inspector that was trying to make me remove some unused/abandoned NM cables in a wall. I told him where the only places the code mentioned "abandoned". He had to call his boss to verify that I was correct.
The code I'm thinking of, I don't think it actually mentions the word abandoned. I believe it says something about not having to remove them, but having to isolate them from the source.
Anybody know the code reference that mentions what to do with abandoned circuits? I remember seeing it in there before, but can't find it now.
I don't believe that there is such a rule in the NEC.... I believe it says something about not having to remove them, but having to isolate them from the source.
If they are still energized the general rules that would apply to conductors in use still apply, as in they should end in some enclosure, fitting, etc. and that enclosure should have cover(s) installed......The code I'm thinking of, I don't think it actually mentions the word abandoned. I believe it says something about not having to remove them, but having to isolate them from the source.
If they are still energized the general rules that would apply to conductors in use still apply, as in they should end in some enclosure, fitting, etc. and that enclosure should have cover(s) installed......
In general - chapters 1-4.Do you know what code that is?
In general - chapters 1-4.
If you have something energized or easily able to be energized it is not really abandoned and you would need to follow whatever section(s) that apply to what you have.
I did say if it is energized or can easily be energized that it isn't exactly "abandoned".I looked all through requirements for electrical installations and the receptacle section and couldn't find anything mentions removing or abandoning circuits.
I did say if it is energized or can easily be energized that it isn't exactly "abandoned".
You found exactly what the NEC does say about abandoned circuits - nothing (that is for in general application, some have pointed out a very limited number of specific instances where something is mentioned on the topic, but only applies to those specific instances)
You may be thinking "redundant" ground. Which is not a term used by NEC, but many use that term to describe what is required from art 517.13(A) for health care facilities.I guess its one of those cases were the state exam asks a question that's not in the code book, like infinite ground I know that's not in there either. But I could have sworn I seen it in the code book when I took the test before.
I don't like it when a NEC question on such an exam uses terms that are not used in the NEC, and think it is a little unfair to those taking the exam to use such terms.
In general - chapters 1-4.
If you have something energized or easily able to be energized it is not really abandoned and you would need to follow whatever section(s) that apply to what you have.
It doesn't necessarily have to be terminated, but it would still be required to be in a chapter 3 wiring method, one suitable for the conditions it is subjected to, would require covers for boxes, wireways, or other enclosing methods.Just for the fun of it Kwired, and if you want to, what section of Chapters 1-4 would be violated if a live wire/cable is left abandoned inside the bay of a wall? I could be wrong and off hand, I don't think the NEC requires it to be terminated.