Hello all, I am installing a receptacle for a range that is paired with a range hood with a fire suppression system. The receptacle is fed through an ABB contactor, AF26-30-00-13. The control voltage for the coil from the hood is 120VAC. When testing out the unit today the contactor was not functioning properly.
When I looked closer at the labeling I also see: 100-250V50/60HZ-DC. When I look up the part number on the ABB website, from what I see this contactor can be equipped with any one of four different coils for a range of control voltages of either AC or DC.
Initially I just glanced across the 50/60HZ and assumed the 120VAC was correct. I'm concluding now though that this is a DC coil only though. Further research has led me to believe that the 50/60HZ-DC is to designate a range in the frequency of the ripple of the DC voltage.
Am I coming to the right conclusion on this? I don't have a lot of experience on this type of equipment and DC voltage.
Would appreciate more knowledge on the subject. Thanks!
When I looked closer at the labeling I also see: 100-250V50/60HZ-DC. When I look up the part number on the ABB website, from what I see this contactor can be equipped with any one of four different coils for a range of control voltages of either AC or DC.
Initially I just glanced across the 50/60HZ and assumed the 120VAC was correct. I'm concluding now though that this is a DC coil only though. Further research has led me to believe that the 50/60HZ-DC is to designate a range in the frequency of the ripple of the DC voltage.
Am I coming to the right conclusion on this? I don't have a lot of experience on this type of equipment and DC voltage.
Would appreciate more knowledge on the subject. Thanks!