Abbreviations explained or Code broken.
A few missing from that list, mostly from the industrial world.
AFC = Available Fault Current
AFD = Adjustable Frequency Drive (same as VFD)
ASD = Adjustable Speed Drive (could be AFD or DC drive)
CP = Control Panel
CPT = Control Power Transformer
CT = Current Transformer (or in a different context, Current Transducer)
DCS = Distributed Control System
DS = Disconnect Switch
FDS = Fused Disconnect Switch
FU = Fuse (or, in a different context, "I don't like you")
FVNR = Full Voltage Non Reversing (as in Starter)
FVR = Full Voltage Reversing (starter)
GUI = Graphical User Interface
HIM = Human Interface Module
HMI = Human Machine Interface
HTR = Heater
ICCB = Insulated Case Circuit Breaker
I-T CB = Instantaneous Trip Circuit Breaker (official term for MCP below)
M = Motor Starter or in a different context, Motor
MCCB = Molded Case Circuit Breaker
MCB = Mini Circuit Breaker (in a different context compared to Main Circuit Breaker)
MCP = Motor Circuit Protector
MCS = Molded Case Switch
MMI = Man Machine Interface (no longer politically correct, see HMI)
MMS = Manual Motor Starter
MPCB = Motor Protection Circuit Breaker
MPS = Motor Protective Switch
MS = Magnetic Starter
MSP = Motor Starter Protector (same as MPS)
NF (DS)= Non Fused (Disconnect Switch)
NRTL = Nationally Recognized Testing Lab (as in UL)
OCPD = Over Current Protective Device
OL (R) = Over Load (Relay)
PAC = Programmable Automation Controller
PCB = Power Circuit Breaker, or in a different context, Printed Circuit Board
PCP = Pump Control Panel
PLC = Programmable Logic Controller
PT = Potential Transformer
RTU = Remote Telemetry Unit (in a different context from Roof Top Unit)
RVAT = Reduced Voltage Auto Transformer
RVPW = Reduced Voltage Part Winding
RVSS = Reduced Voltage Solid State
RV-YD = Reduced Voltage Wye Delta
SCADA = Supervisory Control and Data Acquisition
SCPD = Short Circuit Protective Device
SSOL = Solid State Over Load (relay)
TCC = Time Current Curve
TFMR = Transformer
T-M = Thermal-Magnetic (as in Circuit Breaker)
TOL = Thermal Over Load
Trafo = Transformer (European)
VFD = Variable Frequency Drive
VT = Voltage Transformer (same as PT)
Z = %Z for transformer impedance (when doing AFC calculations)
Whomever thought that initial silent consonants were a good idea, never anticipated the concept of the dictionary. How do I look up what numonia is, when I can't find it in the N-section?
Yeah, it's Greek to me.