Continuing with my comments on voltage measurement.
To track the path of a circuit greater sensitivity is obtained by measuring the voltage drop along the neutral relative to the potential of the EGC bus at the main panel.
You can get the main panel EGC reference in two ways.
One is to run a wire or extension cord from the EGC bus at the main panel to wherever you want to make a voltage measurement relative to said main panel point.
The second way is to use the EGC wire at the measurement point. This second way requires that the EGC is intact back to the main panel, and that no current is flowing in the EGC. For this thread this is not a good assumption.
This approach of measuring the neutral voltage relative to the main panel EGC bus is only going to be seeing small voltages normally. Thus, I can possibly use a 100 W incandescent rather than a 1500 W heater as the load.
My following sample voltages are read with a Fluke 27 with no filtering. Ideally I should have a narrow band 60 Hz band pass filter at the meter input.
At my main panel the Fluke reads 0 or 1 mV between the Sq-D EGC bus and the neutral bus. At my work bench area, about 50 ft away, the reading is about 3 mV. Also about 3 mV between an extension cord EGC and the bench neutral.
With a 100 W lamp load at the bench area at the lamp outlet neutral to EGC is about
120 mV. Going to a point on the benches closer to the wall the reading is about 50 mV. There are three benches with cascading of power from one to another, not short cords. The lamp was located at the middle bench. I use #8 for 50 ft from the main panel to the bench area. Without making an actual measurement I estimate the #8 drop at about 25 mV.
.