That would not resolve the basic concern. You are not allowed to conceal any portion of a flexible cord because you need to be able to inspect it for damage anywhere along its length.
No arc fault needed.
If your not having an inspection I would be OK with it.
It is readily accessible, Nothing unsafe about it, if its installed properly.
But it is a NEC code violation. 400.8