I have a question regarding NEC 680.26 the adopted cycle we are enforcing at this time is 2017 NEC 680.26 equipotential bonding. My question is this: Is the perimeter bond around the pool (18"-24"/4"-6")for above ground (on-ground) pools required for pools that only have resin support members, but DO have a stainless section and seam tying the (coated non-conductive) corrugated steel shell together? This seam is the only point for a bonding lug attachment. From this point you can attach to other applicable conductive parts or surfaces. My thoughts and interpretation of 680.26 is Yes, because, although there aren't 4 equal points available...there is exposed steel on the pool, and bonding all conductive parts plus a perimeter, would appear to satisfy the perimeter bond requirement and eliminate possible areas of voltage potential differences. I would be glad to email additional pictures and additional information if needed. Now as an inspector and having been on both sides of the "coin", I always try to explain the why behind code sections to better inform contractors, but also to eliminate surprises in the field. I am familiar with the feeling of failing an inspection and not getting a clear answer or direction as to why
I don't want to be "that guy"