Ok, you guys answered my question about the continuous load factor on the heater for this pool, but i am confused again about a few other question I have regarding this if someone can help.
1) After reading the nameplate it says (38a circuit ampacity), (Min. fuse 40a) and (Max fuse 60a). After my calculations it seems a 50a fuse would be fine. Is this ok?
2)The reason I'm asking, is because in class, the instructor told us when it comes to A/C condenser equipment, you should always fuse it at the max because the continuous load factors are already taken into consideration just for A/C condensor equipment. Is this correct? If not, how should condenser equipment be handled?
3)According to the code, do you need a disconnect switch for an above ground pool or is just a GFCI protected circuit fine?
4)Accoring to the code, should above ground pools require these circuits be ran in PVC (ENT)?
1) After reading the nameplate it says (38a circuit ampacity), (Min. fuse 40a) and (Max fuse 60a). After my calculations it seems a 50a fuse would be fine. Is this ok?
2)The reason I'm asking, is because in class, the instructor told us when it comes to A/C condenser equipment, you should always fuse it at the max because the continuous load factors are already taken into consideration just for A/C condensor equipment. Is this correct? If not, how should condenser equipment be handled?