LarryFine
Master Electrician Electric Contractor Richmond VA
- Location
- Henrico County, VA
- Occupation
- Electrical Contractor
If a barrier may divide a box for high and low voltages, why wouldn't it do the same for a wireway?
And that's your opinion; time will tell.That's a bad argument...
690.31(B) includes wireways. What box are you referring to; is that in another code article?If a barrier may divide a box for high and low voltages, why wouldn't it do the same for a wireway?
Great! And looks like you were right on the intent, judging by the 2023. I just think the 2020 wording doesn't get there.The AHJ accepted my argument and approved our installation, so....
In our case we constructed insertable barriers out of 1/4" or 3/8" clear polycarbonate and the AHJ accepted it.Since it's not specified in the NEC I've seen "barriers" fabricated on-site out of whatever scrap was around. Does that make a UL Listed raceway into two separate raceways? Hardly. I've always thought that a "barrier" should be defined as a manufacturer supplied item and not just cardboard cut to fit.
Now if the barrier was an option from the manufacturer and was part of the listing of the raceway that would be a different evaluation.
There is ambiguity in the NEC? Say it ain't so!Great! And looks like you were right on the intent, judging by the 2023. I just think the 2020 wording doesn't get there.
Cheers, Wayne
If you have ideas for better language or other changes, the system is open for the submission of Public Inputs to make changes for the 2026 code until September 7th, 2023. You can use the link below to access the system to submit a PI.I would hope this area gets a review and update in NEC soon. Wanting to use a gutter to keep the wiring safe and neat is a good thing. But then having all this confusion and trouble to meet these unclear requirements, may cause many to just keep using separate conduits, which might result in a messier, less maintainable install, which is not good.
I can't think of a reason why 400VDC optimizer output circuits in the same wireway as 240VAC inverter output circuits and using 600V rated THWN-2 is a safety issue for NEC, even without a barrier. Ditto for residential 600V PV output circuits. 300.3(C) allows this generally, but then 690.31(B) adds the barrier requirement. Doesn't make sense for anything except maybe 1000V or 1500V commercial PV circuits.
FWIW, 1000V DC circuits and 600V THWN-2 are exactly my concern.Doesn't make sense for anything except maybe 1000V or 1500V commercial PV circuits.
I'll have to review if the language has been changed but I think optimizer output circuits are not a problem. Or at least that used to be so. Optimizer output circuits are not PV source or output circuits.I would hope this area gets a review and update in NEC soon. Wanting to use a gutter to keep the wiring safe and neat is a good thing. But then having all this confusion and trouble to meet these unclear requirements, may cause many to just keep using separate conduits, which might result in a messier, less maintainable install, which is not good.
I can't think of a reason why 400VDC optimizer output circuits in the same wireway as 240VAC inverter output circuits and using 600V rated THWN-2 is a safety issue for NEC, even without a barrier. Ditto for residential 600V PV output circuits. 300.3(C) allows this generally, but then 690.31(B) adds the barrier requirement. Doesn't make sense for anything except maybe 1000V or 1500V commercial PV circuits.
But they can have higher voltage than 600V.I'll have to review if the language has been changed but I think optimizer output circuits are not a problem. Or at least that used to be so. Optimizer output circuits are not PV source or output circuits.
Yes but he said 400VDC.But they can have higher voltage than 600V.
I know, but optimizer voltages can be much higher than that and 690.31(B) makes no distinction for voltage. 690.31(B) and 300.3(C) are in obvious misalignment but prudence and common sense would imply that compliance with 300.3(C) be acceptable for DC voltages of 600V or less while 690.31(B) would apply to DC voltages greater than 600V.Yes but he said 400VDC.