rafeequepk said:
In my experience, we used to do AC hipot on Bus bars, Circuit breakers, CTs etc and DC hipot on New MV cables. But i didnt understant what is the significance of following this procedure..Is there any thing wrong in doing a bus bar and CTs hipot with DC voltage apply..?
To charge a MV cable of any signifigant length with a 60hZ AC Hipot you need a huge power suply, the Xc of the cable @60Hz is very low, thats why VLF testing is done.
Xc= 1/(2(pi)fC)
The lower the frequency, the higher Xc (capacitive reactance).
The higher Xc (or resistance across the power supply output), the lower the current/power needed to apply a desired voltage.
60Hz Example:
At 60 Hz. a 1 μF cable has an Xc of 2.65 kOhms
At 22 kV, it requires 8.3 amps of current to test
Total power supply rating must be 183 kVA
0.1 Hz VLF Example:
At 0.1 Hz, the Xc is 1.59 megohms
At 22 kV, the current needed is 14 mA
Total supply power needed is 0.304 kVA
At 0.1 Hz, it takes 600 times less power to test a cable, or any other high capacitance load, than at 60 Hz. At 0.01 Hz, 6000 times higher capacitive loads can be tested than at 60 Hz.