Ac breaker and wire size

Merry Christmas
Status
Not open for further replies.

splinetto

Senior Member
Location
Missouri
AC unit is marked for to use a 50 amp breaker...actual compressor amps was 27......A #8 romex is only good for 40A...Would I need to change the wire to #6 or am I good?....
 
Wire to the min, breaker to the max. If the minimum circuit ampacity was 27 amps and the max fuse or breaker was 50, then I'd run #10 and put it on a 50 amp breaker.
 
mdshunk said:
Wire to the min, breaker to the max. If the minimum circuit ampacity was 27 amps and the max fuse or breaker was 50, then I'd run #10 and put it on a 50 amp breaker.
Is this the 225% rule from 440?.....
 