ultramegabob said:if it says to protect it at 50 amps, then you need to run wire rated for at least 50 amps and a 50 amp breaker.
Is this the 225% rule from 440?.....mdshunk said:Wire to the min, breaker to the max. If the minimum circuit ampacity was 27 amps and the max fuse or breaker was 50, then I'd run #10 and put it on a 50 amp breaker.