Don't ya mean 14 AWG @ 20A?

Look at Table 310.16 and tell me what the amps are for #14 at 60C or 75C.

Then look at the note (*) at the bottom which directs us to 240.4 (D). Read the first sentence in 240.4 (D) that pertains to 240.4(G)
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
He's referring to this Dennis:

Thanks. I don't know how that happened but yes 14 @ 20 amps. Don't know where the = and 9 came from...:-?

I also read his post incorrectly thinking he was was questioning me about 14 @ 20 amps. My fault sorry.
 

danickstr

Senior Member
you thought you hit delete (for the 9) and actually hit =, then you hit 0, thinking you were back at the 2.
:smile:
 