Hopefully this post doesent sound like a rambling brain dump. It’s been a long week running entirely on generator after being hit by a hurricane. This has always been extremely puzzling to me any and info I find online has lots of answers, but no conclusion. Most forums aren’t like this one and questions go unanswered.
I have a 12kW Dual Fuel LP/Gas, Duromax XP12000. I love the generator and runs like a tank. Under most circumstances, the generator starts my AC without issue, with or without load. However, many times, when I turn the thermostat down, the AC won’t start and it doesent even TRY to start. Basically when I turn the AC down, the contactor never pulls in. Even when I manually push in the contactor, it only starts the compressor, but never the fan. The only time it consistently starts is when I start the AC for the first time on generator. After that, it sometimes takes 45 mins to start after a call for cooking, and sometimes it won’t start at all and the only way I can get it to start is by turning off the AC completely for an hour (probably after compressor cools off). Last, I’ve noticed that sometimes if I turn something else on in the house , it will start the generator, but not consistently.
I have power monitoring on my panel and my resting usage for the whole home is normally 1.2 kW, and when my AC condenser is on, my load goes up to about 4.7 kW. The generator usually gives me 123v and 125v, respectively (L-N).
Yesterday, I added a hard start kit, changed the capacitor, and changed the contactor. The hard start hit helped the starting amps but didn’t do anything for the original starting issue.
Condenser: Rheem RP1548AJINA (4 ton, RLA = 18.5, Fan FLA = 2.8A, LRA = 128A, HP = 1/3rd, MCA =26).
Some possibilities I found on other forums include:
* The generator is producing a square sine wave and/or dirty power which isn’t working well with 24v control wiring. (This makes sense, but not sure why the fan doesent start so makes me think something else is stopping the fan. )
* Add a 240v - 240v isolation transformer
* The Ecobee thermostat (smart thermostat) doesent like the type of power it’s getting.
*Use a soft start instead of a hard start hit
* Turn on a resistive load before starting (not a solution but this may be helping already per the above).
* The defrost control and/or time delay on the unit is preventing the condenser from starting on generator due to the power quality.
A lot of the solutions seem to be with power quality, but how do I fix the power quality in a practical way?
I know this isn’t an HVAC forum but it’s filled with people 100x smarter so hoping for any practical input or advice from experience. Trying to turn this into a learning experience and if I’m lucky it will help someone else in the future stuck in a hurricane hell.
Thank You all!
Thank You all!