PetesGuide
Member
- Location
- Foster City, CA, USA; NEC 2014
I'm doing a Wi-Fi AP installation, and in routing the cables to one location, I came across these items, which rather horrified me, but I'm having difficulty finding anything in the code that prohibits anything about the power supply aside from the flexible cord that is part of the equipment. What am I missing?


I got the facilities manager, and he was horrified; removed the lamp, but wasn't sure about what the power supply was, so I looked at it and found it to be an Astron RS-35M, which turns out to be a power supply that is rated for 12VDC at 25A continuous duty/35A peak. No indication from the specs that it's got UL 2043 approval. And the red/black cable does not appear to be plenum rated, and dips down inside a nearby wall, terminating in DC outlets.
The facilities manager and I are looking for everything we can use to back up our desire to remove the power supply, and prohibit anything similar in the future.
(The lamp was apparently there as a semi-permanent work light to support accessing the DC power and coaxial cables supporting multiple two-way radios in the room below.)
All references to NEC 2011.
The power supply has a metal enclosure, but that's not enough to make it permitted under 300.22(C)(3) or isit?? And 400.7 prohibits this. And 400.8(5) doesn't apply here, right? Is there anything about non-listed heat-generating devices in plenum spaces? What about the exposed DC connections? I've never had to deal with section 450 before, but this is a transformer, so does that give us any leverage?


I got the facilities manager, and he was horrified; removed the lamp, but wasn't sure about what the power supply was, so I looked at it and found it to be an Astron RS-35M, which turns out to be a power supply that is rated for 12VDC at 25A continuous duty/35A peak. No indication from the specs that it's got UL 2043 approval. And the red/black cable does not appear to be plenum rated, and dips down inside a nearby wall, terminating in DC outlets.
The facilities manager and I are looking for everything we can use to back up our desire to remove the power supply, and prohibit anything similar in the future.
(The lamp was apparently there as a semi-permanent work light to support accessing the DC power and coaxial cables supporting multiple two-way radios in the room below.)
All references to NEC 2011.
The power supply has a metal enclosure, but that's not enough to make it permitted under 300.22(C)(3) or isit?? And 400.7 prohibits this. And 400.8(5) doesn't apply here, right? Is there anything about non-listed heat-generating devices in plenum spaces? What about the exposed DC connections? I've never had to deal with section 450 before, but this is a transformer, so does that give us any leverage?