I've got an interesting scenario that I've yet to encounter before. A large commercial facility was made "solar-ready" by locating sub panels throughout the facility with enough theoretical space to land the output of an inverter in each one. The potential rooftop array can support say, 4 inverters worth of PV modules.
For utility and incentive program purposes, I need to combine the output of the inverters so I can meter it and provide an open blade disconnect at ground level. The client then wants to de-combine the outputs with a dedicated PV distribution panel that then ties individual output breakers into the individual sub-panels located throughout the facility. The sub-panels feed other loads, and all of them are eventually fed by a 3000A switchgear.
Aside from the backfed breakers not being at the end of the bus, this feels like a violation of the NEC, but I can't quite determine where to start. Since there is no feasible way to throttle the output of the inverters to match the loads in each sub-panel, and there's no way to direct electrons once they get into the AC PV distribution panel, I can envision a scenario where breakers start tripping in a cascading manner because the inverters start ganging up on loads, tripping that particular breaker in the PV distribution panel, then going to the next, then the next, then the next, etc.
Then if the voltage drop values of the feeders between the sub-panels and the main gear are not dead nuts across the board, could that cause issues too with one inverter sub-panel feeding another?
I've designed plenty of systems that interconnect to individual sub panels across a complex, but never had to combine them first, then try to uncombine them.
Again, it feels wrong. Just not sure where to start. And for what it's worth, the inverter sizes are not uniform.
Snippet of part of the drawing attached.
For utility and incentive program purposes, I need to combine the output of the inverters so I can meter it and provide an open blade disconnect at ground level. The client then wants to de-combine the outputs with a dedicated PV distribution panel that then ties individual output breakers into the individual sub-panels located throughout the facility. The sub-panels feed other loads, and all of them are eventually fed by a 3000A switchgear.
Aside from the backfed breakers not being at the end of the bus, this feels like a violation of the NEC, but I can't quite determine where to start. Since there is no feasible way to throttle the output of the inverters to match the loads in each sub-panel, and there's no way to direct electrons once they get into the AC PV distribution panel, I can envision a scenario where breakers start tripping in a cascading manner because the inverters start ganging up on loads, tripping that particular breaker in the PV distribution panel, then going to the next, then the next, then the next, etc.
Then if the voltage drop values of the feeders between the sub-panels and the main gear are not dead nuts across the board, could that cause issues too with one inverter sub-panel feeding another?
I've designed plenty of systems that interconnect to individual sub panels across a complex, but never had to combine them first, then try to uncombine them.
Again, it feels wrong. Just not sure where to start. And for what it's worth, the inverter sizes are not uniform.
Snippet of part of the drawing attached.