AC Disconnect (2023)

psimmond

Member
Location
Georgia
Occupation
Building Inspector
The new code language in 440.14 specifies 110.26(A), so it would seem 110.26(E) should not be applied. So a line set running horizontally secured to the wall below the disconnect would be fine as long as it doesn't project out beyond the face of the disconnect, right?
 

Bill Snyder

NEC expert
Location
Denver, Co
Occupation
Electrical Foreman
If it's not likely to be worked on while energized then it wouldn't matter I use a non fused pullout switch for that reason.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
If it's not likely to be worked on while energized then it wouldn't matter I use a non fused pullout switch for that reason.
All disconnects are likely to be examined while energized, as they are the very first place most troubleshooters will start with...verification of power at the load side of the disconnect.
The new language in 440.14 bypasses the parent text of 110.26(A) and directly specifies compliance with the specified work spaces in the second level subdivisions of 110.26(A).
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
All disconnects are likely to be examined while energized, as they are the very first place most troubleshooters will start with...verification of power at the load side of the disconnect.
I agree. Here in NJ we have a local amendment that says that AC disconnects are not required to meet the working space outlined in 110.26 which is dumb for the reason that you've mentioned. One of the first things you'll check when troubleshooting an AC unit is you'll start at the disconnect instead of opening up the entire unit. Fused or non-fused doesn't really change anything,
 

Jaybone812

Member
Location
Massachusetts
Occupation
Electrician
If it's not likely to be worked on while energized then it wouldn't matter I use a non fused pullout switch for that reason.

440.14 says the working space clearance for ac disconnects must meet the required working space listed in 110.26(a) . Doesn’t say ac disconnects shall be installed in accordance with 110.26(a) , if it did then the likelihood of it being worked on while energized would factor into the amount of required working space . But the article says the working space for the disconnect shall meet the required working space that’s listed in 110.26(a) , which makes the likelihood of energized service irrelevant


Sent from my iPhone using Tapatalk
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
But the article says the working space for the disconnect shall meet the required working space that’s listed in 110.26(a) , which makes the likelihood of energized service irrelevant
But prior to the 2023 NEC working space was only required if the disconnect was tested, etc. while energized. It has long been argued that it does not require testing etc. therefore the working space was not required in earlier code versions.
 

Jaybone812

Member
Location
Massachusetts
Occupation
Electrician
But prior to the 2023 NEC working space was only required if the disconnect was tested, etc. while energized. It has long been argued that it does not require testing etc. therefore the working space was not required in earlier code versions.

Prior to 2023 the conditions in 440.14 were a readily accessible location within sight of the equipment. Working space in 110.26 (a) never played a factor


Sent from my iPhone using Tapatalk
 

Jaybone812

Member
Location
Massachusetts
Occupation
Electrician
Something readily accessible doesn't automatically meet the definition of working space.

440.14 in nec editions prior to 2023 did not require any specific clearances or dedicated working space around ac disconnects . Prior to 2023 nec 440.14 required us to install the ac disconnect in a readily accessible location that was within sight of the equipment . Allot of inspectors tried to enforce the code rule like the working space required by 110.26(a) was mandatory . But a specific amount of working space was never required prior to the 2023 cycle . It’s only required to be within sight and readily accessible .


Sent from my iPhone using Tapatalk
 

Ken_S

Senior Member
Location
NJ
Occupation
Electrician
I'll have to look for it when I get back to my office. It did say amendment but it might actually be from the DCA Code Communicator where they made an interpretation as to it not being required in NJ.
Found it, this only applies to existing installs for a replacement:

Air-Conditioning Disconnects Does Section 110.26 of the 2002 National Electrical Code (NEC) apply when an air-conditioning unit is being replaced?

N.J.A.C. 5:23-6.8(d)2 in the Rehabilitation Subcode excludes Section 110.26 of the 2002 NEC. This applies to working clearance space around electrical equipment. However, Section 440.14 of the 2002 NEC is not excluded under N.J.A.C. 5:23-6.8(d)5. This section states that the disconnecting means shall be located within sight of, and readily accessible from, the air-conditioning or refrigerating equipment. The disconnecting means is permitted to be installed on or within the air-conditioning or refrigerating equipment.
Therefore, the answer is NO, Section 110.26 of the 2002 NEC is not applicable to units that are being replaced. Any existing disconnect shall be permitted to remain, provided that the disconnect is in sight of the unit and readily accessible; i.e., nothing has to be moved to access it.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
But prior to the 2023 NEC working space was only required if the disconnect was tested, etc. while energized. It has long been argued that it does not require testing etc. therefore the working space was not required in earlier code versions.
Yes, prior to the 2023, that was up to your AHJ. In many areas, the AHJs have been requiring compliance with the 110.26 work spaces for a long time, but in other areas, they have not.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Yes, prior to the 2023, that was up to your AHJ. In many areas, the AHJs have been requiring compliance with the 110.26 work spaces for a long time, but in other areas, they have not.
Exactly. Which is odd because opening the disconnect and testing for voltage is one of the first things you do when troubleshooting these types of units.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
I know. I'm glad that they actually wrote the language into the 2023 NEC. I'm thinking that the substantiation was exactly what we're discussing.
The substantiation was:
For many years there have been some confusion among Electrical and HVAC contractors, as well as Inspectors. I am proposing to add verbiage to article 440-14 to include "Disconnecting means shall meet the working space requirements of 110.26(A)(1) through (A)(3)" for clarification purposes. Thank you for your consideration.
The panel statement was:
A reference to 110.26(A) is being added to the normative text of 440.14 to emphasize the importance of complying with 110.26(A) when locating HVAC disconnecting means. This subsequently will eliminate the need for informative note 2.
The PI actually eliminated the reference to the parent text to be sure that was not applied.
Disconnecting means shall meet the working space requirements of 110.26 (A)(1) through (A)(3).
The panel changed the reference to just 110.26(A).
 