All - Please see the attached pic of the AC disconnect on this 3-line. This is for a 208/120 3P job we have pending. For reference, this is an Enphase system with two separate rooftop systems, each with it's own load center combiner panel. One has a combined output of approx 90A, the other approx 100A. The circuit designer took the outputs of the two AC combiners and combined them together on the input terminals of the 400A non-fused AC disconnect (circled in red). I personally have never seen this done and also couldn't find an AC disconnect with multi-wire terminals. They suggested we could use 3-port Polaris or similar splices to combine the 2 outputs into a pigtail to attach to the disconnect. This brings up several questions:
1) Are there any code violations or code language that addresses this? Since both the line and load side of the AC disco have OC protection, I don't see an issue there. As for ampacity, all of the wiring meets the ampacity requirements so I don't see any issue there either, including making sure the combined pigtail wire on the Polaris is sized to carry the combined current into the AC disconnect.
2) Has anyone done this before and if so, what listed hardware did you use to make the combined connection into the disconnect?
I know this probably seems simple but normally, if we needed multiple solar systems combined into a single source output, the plans would typically land each system's AC output onto individual breakers in an MLO load center that feeds the AC disco and onto the point of interconnection.

1) Are there any code violations or code language that addresses this? Since both the line and load side of the AC disco have OC protection, I don't see an issue there. As for ampacity, all of the wiring meets the ampacity requirements so I don't see any issue there either, including making sure the combined pigtail wire on the Polaris is sized to carry the combined current into the AC disconnect.
2) Has anyone done this before and if so, what listed hardware did you use to make the combined connection into the disconnect?