I got a red tag from an inspector telling me my breaker size was too small for the ac unit. The nameplate on the unit says 26.1 minimum ampacity
40ampHACR / 45AMP FUSE.
I have a 2P 30 HACR breaker with a non-fused disconnect.
This has been legal for many years has is changed and I just missed it. Inspector was 40A.on the branch circuit.
40ampHACR / 45AMP FUSE.
I have a 2P 30 HACR breaker with a non-fused disconnect.
This has been legal for many years has is changed and I just missed it. Inspector was 40A.on the branch circuit.