Re: AC equipment 440
AC units under Article 440 need to have there OCPD and conductors sized according to the nameplate on the unit. This nameplate must include:
Minimum Circuit Ampacity
Maximum Fuse or Circuit Breaker
It is not uncommon to see #12 wire protected at 30, 35 or even 40 amps. The conductors are sized according to the MCA not the maximum overcurrent protection device size.
According to table 310.16, #12 THHN can supply a minimum circuit ampacity of 25 amp or less.