hhsting
Senior Member
- Location
- Glen bunie, md, us
- Occupation
- Junior plan reviewer
Attached MLO main service switchboard is service entrance rated equipment 208/120V three phase 4000A. The main service switchboard is MLO and has Six main service disconnects breakers feeding loads in residential apartment complex building four floors.
In the picture there is note #29 which says to provide 800AF space provision for future PV system feedback breaker in addition to the six main service breakers.
Following questions:
1. Would the note #29 PV system backfeed breaker be counted as seventh disconnect or not based on NEC 2017?
2. As of right now its 800AF space can that count towards six main service disconnect rules?
3. Does MLO service entrance rated equipment with sections as shown in picture come with eight disconnects?
4. From the way I see it the future PV system feedback breaker would be connected In the main service disconnects Not ahead of main service disconnecting means. Correct or incorrect
In the picture there is note #29 which says to provide 800AF space provision for future PV system feedback breaker in addition to the six main service breakers.
Following questions:
1. Would the note #29 PV system backfeed breaker be counted as seventh disconnect or not based on NEC 2017?
2. As of right now its 800AF space can that count towards six main service disconnect rules?
3. Does MLO service entrance rated equipment with sections as shown in picture come with eight disconnects?
4. From the way I see it the future PV system feedback breaker would be connected In the main service disconnects Not ahead of main service disconnecting means. Correct or incorrect