Okay, for both of you...
A PV source on the line side of all load breakers cannot increase the maximum current that the loads draw. That current is limited by the load breaker(s), whether that current is supplied by the utility, the PV or some combination of both.
Further, the service conductors cannot carry current in two directions at the same time. The maximum current that can be 'imported' is the maximum load. And the maximum that can be 'exported' is the PV max output if there is zero load. Article 230 sections mentioned above covers overload protection for import current. Article 705 language mentioned above provides protection against 'export' overload. In other words, as long as the service is rated for the larger of the 'import' or 'export' need then it is protected, and these two requirements never add to each other.
hhsting, the PV in this case is fine because it is less than the service rating. The sum of the load breakers exceeds the service rating, but this may be allowed by the above mentioned exception in 230.90(A). It is completely legitimate to ask an engineer to provide documentation that the calculated load (per Art. 220) is less than the service rating. However the PV does not add to the load, and has nothing to do with that. If the loads are all existing and were compliant when installed then the PV changes nothing about them.
augie, on the load side of the service disconnect means it is possible for an interactive source to defeat upstream overcurrent protection in various ways by possibly adding to the max current that can be provided by the utility through that overcurrent protection. Hence the complicated 705 rules for load side connections. This isn't possible for supply side connections because there is no upstream overcurrent protection to defeat. Hope that makes sense.