AC Unit Brain Fart

Status
Not open for further replies.

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician (retired)
I'm trying to recall what the function is of the two wire cable that goes from the AC blower unit in the attic to the AC compressor unit outside (not a mini split). Does this control 2-wire cable provide 24 volts to close the relay at the outside unit or is it just for a contact that closes when calling for AC with the 24 volts coming from the outdoor unit?
 
In modern systems, the 24v comes from the air handler, and energizes the compressor contactor.
 
Status
Not open for further replies.
Top