Hello Forum,
I'm trying to size the OCPD and conductors for a direct expansion air conditioning unit. The mechanical engineer has told me the indoor unit is rated: 460V, 3phase, 60hz with FLA 66 A, MCA 74 A and MOP 90 A. There is also a reheat which is 22.5 kW. Here are my calcs.
Circuit Size:
(66 amps x 1.25) + (22.5kW/(480V x 1.732)) = 109.56 A
I've selected #2 conductor.
OCPD:
(66 A x 2.25) + (22.5kW/(480V x 1.732)) = 175.56 A
I selected a 3P175A circuit breaker.
I'm concerned because this seems breaker seems rather large for a branch circuit breaker. Can anyone verify if I'm doing this correctly? Any comments is greatly appreciated.
Thanks