southernboys#2
Member
Hey guys on an ac unit if its marked for a min circuit ampacity of 30a is there any exception that would allow me to pull #12 wire and be protected by a 30a breaker? My boss tried to throw in a 10% percent rule to justify the 12 awg wire. I think he meant the 110% rule that applies to some motors but not those with a min nameplate rating. Could use some clarification