Because I'm lazy and hope someone else has done the analysis I'll ask first;
What are the economics of utilizing a DC combiner box at the array, and running a 2 wire DC circuit (2//#4/0AWG) to the inverter from the combiner box using a larger Inverter say 166KW, versus utilizing smaller inverters (3 x 50KW) with built in string connection capability (SMA) and running ckt as #1AWG, 3ph AC circuit from each inverter to power panel?
There as equipment cost considerations but also installation and labor cost that need to be factored.
Thanks
What are the economics of utilizing a DC combiner box at the array, and running a 2 wire DC circuit (2//#4/0AWG) to the inverter from the combiner box using a larger Inverter say 166KW, versus utilizing smaller inverters (3 x 50KW) with built in string connection capability (SMA) and running ckt as #1AWG, 3ph AC circuit from each inverter to power panel?