Hi everyone, Question on voltage drop calculations. I understand vd and the calculations and use them alot in the field and school. My question is, when you figure vd out on, lets say a parking lot lighting project. 4 lights in a row. 4 amps per pole@ 208 volts. First pole @ 200 ft then each pole 100ft between each other for a total of 500ft. Now on a purley resistive ck the current drops off at each pole so at the last pole there is no current. The first pole would be #10 wire then after the 2nd pole the cm goes down even thought the distance increases. I have always taken the calculation to the last pole first which makes the conductors larger. On a purley resistive load the conductors will be smaller. Now on an non-linar load such as parking lot lights how do you all calculate your voltage drop? Because of the inductance should the Neutral not be dropped? Confused a bit. Please help. Thanks Mike