Not at the appliance. Not everyone agrees with that.So at 64 VA and no compressor or you saying the air handler doesn't need a disconnect? Thank you
My perspective:
It doesn't have a hermetic refrigerant compressor - so art 440 doesn't apply to it.
That leaves us with art 422 being the main code that applies to this equipment. 422.31(A) allows the branch circuit device to be the disconnecting means (regardless of where it is located) for permanently connected appliances not over 300 VA or 1/8 HP.