Given that the OP's looped conductors are spliced, they'd count as two.Would looping the conductors and continuing them on to the next box without cutting, have any effect on calculating box fill?
Would the looped conductors be counted as one or two?
2008 NEC
314.16(B)(1)
. . . Each loop or coil of unbroken conductor not less than twice the minimum length required for free conductors in 300.14 shall be counted twice. . . .
This was your original concern.
Is it the tab you are worried about or the screws?
The concern is the screw connection increasing in impedance to the point that the connection overheats.
By removing the outlet itself as a feed to downstream loads, failure modes such as these can be avoided.
It is one less knot to fail.
It's actually one less wire in the box. Whether we required to count it or not.
I've never seen or done this peronally......BUT one benefit I can possibly see from the OP's method is like was said earlier if you lose one receptacle from a bad connection or whatever may be the case the ones downstream would not be affected, and that in turn could help speed up troubleshooting if it came to that. I'd be a little curious/concerned how it would work out rolling up loops in a box attached to the receptacle though.
As the OP described the installation, the 'mid span' stripped area was near the end of one piece of wire (say coming from a conduit or cable), and continued on to a wire-nut which was used to make a splice to another piece of wire, going on to the next part of the circuit.
-Jon
You won't lose downstream receptacles if you pigtail each receptacle.
hurk27 in post#20 mentions yet another approach, which eliminated the wire-nut splice. In this case, the conductor enters the box, is mid-span stripped and looped on the device, and then exits the box, without ever being cut or spliced. Here I can see a tangible benefit of having no splice in the wire to fail at all. I am not in a position to argue cost versus benefit of the more difficult stripping versus the elimination of a wire-nut, but it sounds like a reasonable approach to me. I bet that in areas where this is done frequently, people get good at quickly stripping the middle of runs.-Jon
I got real good at it, using the proper size stripper hole on the wire strippers, just cut the insulation in two places about an 1" apart, then using your lineman's clamp down on the insulation that is being removed, pinching it against the wire, then pull off the section of insulation, bend in the middle of the bare spot, and crimp around screw, tighten and your done.![]()
Connect wires per WIRING DIAGRAM as follows:
NOTE: Side wire terminals accept up to #10 AWG
wire.
TO SIDE WIRE:
? Loop wires clockwise 3/4 turn around terminal
screws.
? Green or bare copper wall box wire (Ground)
to Green screw.
? Line 1 Black (Hot) wall box wire to Brass screw.
? Line 2 Black (Hot) wall box wire to remaining
Brass screw.
? White (Neutral 1) wall box wire to Silver screw.
You're right....brain fart...:roll: