Acceptable unbalanced load current

Status
Not open for further replies.

MFS-PDX-313

Member
Location
Tualatin, Oregon, USA
Occupation
Electrical design engineer, Industrial equipment
working on a project for a customer. They are supplying three-phase 208 wye. I've got various loads in the circuit: some are single-phase line to neutral, some are three-phase, and a couple of them are single-phase line to line. I did my current calculations and I have 39.3A on L1, 27.0A on L2, and 26.3A on L3. Is there some regulation or standard that says what the limit is to unbalancing loads like this?
 
In a largely-single-phase-load environment, constant large changes in load balance are unavoidable.
 
I did my current calculations and I have 39.3A on L1, 27.0A on L2, and 26.3A on L3. Is there some regulation or standard that says what the limit is to unbalancing loads like this?

There is nothing wrong with these numbers, they're just part of having 1Ø loads.
 
I came across this: http://www.hvac.amickracing.com/Electrical Information/Current Unbalance.pdf

It also says that 10% is the maximum acceptable unbalance for current, but is that for a single load?
That is only for the current going into the actual load...has nothing to do with the balance on the electrical supply system.

There is no issue with your current balance on your panel. It is impossible to get the loads balanced when they are in use because they are not all on at the same time.
 