10-38 Log #2936 NEC-P10
Final Action: Reject
(240.24(B))
Submitter: Philip Simmons, Simmons Electrical Services
Recommendation: Revise existing 240.24(B) as follows:
(B) Occupancy. Each occupant shall have ready access to all overcurrent devices protecting the conductors supplying that occupancy. Enclosures housing electrical apparatus that are controlled by lock and key shall be considered accessible to qualified persons.
Exceptions to remain unchanged.
Substantiation: This is a companion proposal to delete the rule from 110.26 and add it to 230.92 and 240.24(B). 110.26 deals with access to working space about electrical equipment and does not apply to access to the equipment itself. It seems the provisions on electrical apparatus controlled by a lock and key would more properly be located in 230.92 and 240.24(B).
Many locations come to mind where electrical equipment is locked to prevent unauthorized access. These include schools, colleges, health care facilities, airport terminals and office buildings that are open to the public. These buildings often have either panelboards with locking covers or electrical equipment located in locked rooms. Electrical inspectors recognize the security that is needed in these and other facilities. Locating this rule with the sections that cover locks on equipment will improve the usability of the Code.
Panel Meeting Action: Reject
Panel Statement: The introductory sentence to 240.24(B) focuses on accessibility by each occupant. The subsequent exceptions also focus on each occupant. It is inappropriate and confusing to add this sentence dealing with qualified persons. Further, deleting this accessibility permission from110.26 and moving it to this article and 230.92 will place further restrictions on where a lock limits accessibility.
Number Eligible to Vote: 12
Ballot Results: Affirmative: 12