Accessible GFCI devices?

Status
Not open for further replies.

mlnk

Senior Member
I think the 2017 NEC requires all kitchen receptacle outlets to be GFCI protected-not just counter top receptacles. Can the GFCI for a DW or disposal or trash compactor be located under the sink? Is that considered accessible?
And if an upstream device is mounted on the backsplash does it need to be a blank face type?
Also, for the garage door opener receptacle the ceiling mounted device is not accessible, so does it need to be downstream from a wall mounted GFCI? If inspector requires a separate circuit for the GDO, does this mean the GFCI on the wall needs to be a blank face type?
 
Many inspectors consider under the counter to be accessible as long as it is not blocked by permanent storage shelves. But do not count on that. :)
Yes, a GDO that cannot share a circuit and must have its receptacle on the ceiling will require either a GFCI breaker or a dead front in an accessible location.

Not sure what your question is about the backsplash.

Sent from my XT1585 using Tapatalk
 
I think the 2017 NEC requires all kitchen receptacle outlets to be GFCI protected-not just counter top receptacles. Can the GFCI for a DW or disposal or trash compactor be located under the sink? Is that considered accessible?
And if an upstream device is mounted on the backsplash does it need to be a blank face type?
Also, for the garage door opener receptacle the ceiling mounted device is not accessible, so does it need to be downstream from a wall mounted GFCI? If inspector requires a separate circuit for the GDO, does this mean the GFCI on the wall needs to be a blank face type?

All receptacles in the kitchen is not true. 210.8(A)(6) requires protection for receptacles serving countertops. (A)(7) requires protection for receptacles within 6 feet of sinks. 210.8(D) requires protection for the dishwasher. Those are the most common conditions in a dwelling kitchen where GFCI is required, most anything else in the kitchen doesn't require GFCI protection.

GFCI devices need to be readily accessible - some don't think inside a cabinet is readily accessible, I think that is pushing the rules a little. If you needed 110.26 clearances to call it readily accessible (some think that is necessary) then they shouldn't be allowed to be located above counter spaces either.

Only reason to require "blank face" devices is in situations where no other outlets are allowed on the circuit with the protected outlet(s) or similar situation.
 
I think the 2017 NEC requires all kitchen receptacle outlets to be GFCI protected-not just counter top receptacles. Can the GFCI for a DW or disposal or trash compactor be located under the sink? Is that considered accessible?
And if an upstream device is mounted on the backsplash does it need to be a blank face type?
Also, for the garage door opener receptacle the ceiling mounted device is not accessible, so does it need to be downstream from a wall mounted GFCI? If inspector requires a separate circuit for the GDO, does this mean the GFCI on the wall needs to be a blank face type?


Not all kitchen receptacles have to be GFCI protected unless commercial kitchens. If stove, microwave, trash compactor, and fridge is out of the 6’ range then you don’t need GFCI protection.
 
Not all kitchen receptacles have to be GFCI protected unless commercial kitchens. If stove, microwave, trash compactor, and fridge is out of the 6’ range then you don’t need GFCI protection.
If the receptacle for those items is more then 6' from the sink, and also is not serving countertops it doesn't need GFCI protection, in dwelling kitchens.
 