brycenesbitt
Senior Member
- Location
- United States
Physics wise -- the only thing that keeps the connection from corroding is initially it's gas and water tight, due to the compression face to face copper to steel. That's it.Good question. Looking around I can find similar clamps that say they are rated for copper, galvanized, stainless or steel rods,rebar, etc. which makes sense for the clamp itself that is usually bronze, but what keeps the copper conductor that is in direct contact with the rod from having galvanic corrosion with the steel rod? Most other clamps listed for use with rebar have separate contact surfaces for the rod and the conductor and the rod and conductor are not in direct contact within the clamp.
But we all know that rebar rusts quite quickly even without help, and anything near the ground is going to be wet. Eventually that rust will reduce the margin of contact as it eats between the steel and copper.
Galvanic corrosion happens at very low voltages: like tenths of a volt. And you can easily have that voltage difference between true ground and the GEC. You thus have all the elements of galvanic corrosion. The steel will be the sacrificial anode, the copper and brass will be fine.
Cathodic protection - Wikipedia
In field inspections this effect is very pronounced near water heaters (inside and out). Encased in concrete who knows? Concrete is porous to water vapor and moisture and is conductive. Maybe we just throw away buildings in the USA too fast to notice. Go to the UK with 900 year old pubs and inns, and find the one with the oldest ground connection and check.....